Like I said, a solution in search of a problem.What is the purpose of rain tight fitting anyway when the old one worked fine and the conductors in the conduit are THWN anyway?
Like I said, a solution in search of a problem.What is the purpose of rain tight fitting anyway when the old one worked fine and the conductors in the conduit are THWN anyway?
Many guys do not know that there are two types of compression fittings and think all of them are rain tight..
That is a better answer than what I had in mind. They were all rain tight before someone discovered they could put an additional nylon ferrule inside and a gasket at the base and thought it was better. There is still more water from condensation involved in most installs than the "non raintight" compression fittings will ever allow to leak into the raceway.:thumbsdown:Like I said, a solution in search of a problem.
Running emt outdoors is bogus.
Agreed. Steel EMT is just as galvanized as steel RMC, and it usually ends up getting painted, providing just a bit of extra protection from the elements. Unfortunately, it seems that many people see EMT as an indoor-only wiring method; I've seen a few sets of standard specs for different facilities we've designed for that specifically prohibit EMT from being installed outdoors. But hey, I guess if they really want to pay for RMC instead...Why do you think that? I would take emt over pvc any day of the week and many jobs dont have the budget for rmc or imc
Agreed. Steel EMT is just as galvanized as steel RMC, and it usually ends up getting painted, providing just a bit of extra protection from the elements. Unfortunately, it seems that many people see EMT as an indoor-only wiring method; I've seen a few sets of standard specs for different facilities we've designed for that specifically prohibit EMT from being installed outdoors. But hey, I guess if they really want to pay for RMC instead...
RMC will corrode also, just has a heavier wall to corrode away before it gets a hole in it.
I generally don't see RMC/IMC rust out either. I do see increased corrosion underground, but seldom complete disintigration. Most EMT I see issues with would generally last longer if better care were taken on installing it. That "shall be arranged to drain" wording definitely applies to many of those installs. I do see some increased corrosion in RMC/IMC that has not been arranged to drain either.In this area of the country EMT exposed to the weather rusts away much quicker than RMC or IMC.
http://education.randmcnally.com/cl...rMapImage.do?mapFileName=RMC_US_Acid_Rain.png
Most of our job specs prohibit running EMT outside.
I don't want to get into a long drawn out discussion here but I don't see RMC or IMC rusting out except where feild threaded and not recoated.