This is kind of my question, and thanks for simplifying it. That would make sense to me but, 250.50 states 'All grounding electrodes as described that are present shall be bonded together to form the GES.'Sorry, if:
- There's an unspliced GEC from the meter base to a ground rod, so that the CEE only needs a bonding jumper, not a GEC.
- And given the service size #4 Cu is sufficient for the CEE.
- And there's a #4 Cu from the CEE to the ground bar in the interior panel
- And there's a #4 Cu or bigger EGC in the feeder from the service disconnect to the interior panel
Then what's the code violation?
Cheers, Wayne
THANK YOU