It should have said 250.64(F), and I don't see it as complying with any of the 3 permissions there.How's that? The only requirement in (2017) 250.65(F) for bonding jumpers is the reference to 250.53(C), which I already discussed compliance with.
Cheers, Wayne
(1) permits the bonding jumper to be run to another grounding electrode....does not do that
(2) permits each grounding electrode to have its conductor run to the service equipment individually....does not do that
(3) permits multiple bonding jumpers from multiple grounding electrodes to be connected at a 1/4 x2" bus bar....does not do that