Fred B
- Upstate, NY
- Electrician
What is that neutral just hanging out at bottom?
Excuse me, not overly familiar with VFD just the basics, If I am to understand what you're saying and it's relationship to the OP issue, the VFD causes a potential harmonic that will intermittently trip the AFCI. Would I be correct to assume, for it to be random as OP indicated most likely the circuits tripping had some form of load at the time the VFD activated, otherwise there would be no appearance (from AFCI or GFCI perspective) of an imbalance. No load no Arc or ground fault. Is this a correct assumption? Or is there some other action at play?I seriously doubt that the transformer is your problem but it absolutely needs to be replaced with the proper one.
From your saying that you hear the fan "ramp up", it would indicate a VFD which are notorious for messing with AFCIs and GFCIs.
-Hal