I was pretty certain there was 50 amp OCPD limit somewhere, but though maybe was in 210. Looks like it is what you mentioned though in 422.
There's not a maximum limit in Section 210. Section 422 doesn't provide a maximum limit unless the range has a demand of more than 60A. And then the manufacturer would have to subdivide the load.
 