jwelectric said:Well George the way I figure it is that Table 220.55 goes all the way up to 61 ranges and over.
Mike we are not talking about 61 ranges we are talking about one particular range on a branch circuit.
jwelectric said:Well George the way I figure it is that Table 220.55 goes all the way up to 61 ranges and over.
I can not for the life me comprehend why you see it as this;
For ranges of 8? kW or more rating, the maximum branch-circuit rating required shall be 40 amperes.
Mike I am not being a wise @8% I am truly lost as to you thoughts on this section.
Branch-circuit conductors supplying household ranges, wall-mounted ovens, counter-mounted cooking units, and other household cooking appliances shall have an ampacity not less than the rating of the branch circuit and not less than the maximum load to be served.jwelectric said:The first sentence of 210.19 seems to be throwing you thoughts off kilter just a little.
Can you restate this statement more clearly? What are you trying to say?jwelectric said:It is the second sentence that wraps the circuit for a single range and it clearly states that a minimum circuit of 40 amps for ranges 8 ? kw and larger.
In a prior post said:What is the point of going to the trouble of all that math, if you're always allowed to just install a 40A circuit and forget about it? You're not making any sense, think about it. What's the point of allowing us to calculate a branch circuit load according to a demand table, if we can overlook the results and just put in a minimum?
Mike, you are adding something to that last sentence. You are changing the word "minimum" to maximum. There's no two ways about it.jwelectric said:The way I read it is that I could install a 27kw range on a 40 amp circuit
georgestolz said:Mike, you are adding something to that last sentence. You are changing the word "minimum" to maximum. There's no two ways about it.jwelectric said:The way I read it is that I could install a 27kw range on a 40 amp circuit
But that's what you're saying, for a range.
The minimum service size to a dwelling unit is 100 amps. Does that mean that if a load calc comes out to 195 amps, you can install a 100 amp service, because code says minimum is 100?
This is different that the minimum size service required in 230.79(C) in that 210.19(A)(3) gives the size limitation of the range. It says anything that is 8 3/4 kw and larger.
If the load is over 9.6 kW you can't use the minimum branch circuit rating.(3) Household Ranges and Cooking Appliances Branch-circuit conductors supplying household ranges, wall-mounted ovens, counter-mounted cooking units, and other household cooking appliances shall have an ampacity not less than the rating of the branch circuit and not less than the maximum load to be served. For ranges of 8 3/ 4 kW or more rating, the minimum branch-circuit rating shall be 40 amperes.
don_resqcapt19 said:First Article 220 has nothing to do with the selection of conductor size. ................If the load is over 9.6 kW you can't use the minimum branch circuit rating.
Don
This last sentence clearly states that the MINIMUM circuit allowed for a range 8 ? kw or more RATING is 40 amps
jwelectric said:9600/240 = 40 amps
210.19 Conductors ? Minimum Ampacity and Size.
(A) Branch Circuits Not More Than 600 Volts.
(1) General. Branch-circuit conductors shall have an ampacity not less than the maximum load to be served.......
I agree with Don, George and Rick that what that means is 8.75 KW to 9.6 KW will be supplied by at least a 40 amp circuit.
Do you think your interpretation makes the least bit of sense? :?
jwelectric said:I have a hard time believing that anyone can not see the words as they are written.
jwelectric said:It is very clear to me that the intent was to allow a 40 ampere circuit to be installed for any one range or the wording of that sentence would have been different to reflect the thought of 8.75 through 9.6kw.
Now I am going to church.
jeff43222 said:Now that we're all in agreement and everything's been cleared up...![]()
Would anyone care to venture an opinion as to what size circuit I should install for this 14.4 kW range?