I just got hired to wire up a new electric range, and when I looked at the nameplate and the installation instructions, I wound up unsure as to what size circuit I should install.
The nameplate rating for 120/240V said 14.4 kW. My calculator says that the amperage for such wattage would be 57.5 - 60A (depending on whether you use 240V or 250V). Either way, my thinking was that this installation would call for a 60A circuit.
But the instructions that came with the range called for a minimum 40A, maximum 50A circuit. I don't see how 14.4 kW is possible on a 40A circuit. Sure, I could install for 40A, but if the homeowner cranks the thing up and does a lot of cooking, the breaker would trip long before get gets the 14.4 kW he paid for. Usually when I wire up ranges, the nameplate wattage and the circuit size in the instructions agree with each other.
Or am I missing something here?
The nameplate rating for 120/240V said 14.4 kW. My calculator says that the amperage for such wattage would be 57.5 - 60A (depending on whether you use 240V or 250V). Either way, my thinking was that this installation would call for a 60A circuit.
But the instructions that came with the range called for a minimum 40A, maximum 50A circuit. I don't see how 14.4 kW is possible on a 40A circuit. Sure, I could install for 40A, but if the homeowner cranks the thing up and does a lot of cooking, the breaker would trip long before get gets the 14.4 kW he paid for. Usually when I wire up ranges, the nameplate wattage and the circuit size in the instructions agree with each other.
Or am I missing something here?