Mark it has nothing to do with the size of the OCPD.Originally posted by busman:
Since this is a feeder, it has an OCPD at its origin. The rating of the feeder is the size of this OCPD.
Mark
Russ the feeder and OCPD could be 15 amps only the size of the disconnecting means is mandated by 225.39(D).Originally posted by russ:
The load calculation according to article 220 will determine the feeder and overcurrent size, with 60 amp being the minimum
225.39 Rating of Disconnect.
The feeder or branch-circuit disconnecting means shall have a rating of not less than the load to be carried, determined in accordance with Article 220. In no case shall the rating be lower than specified in 225.39(A), (B), (C), or (D).
This wouldn't work for a service though. Only a feeder. And not a feeder that carries the entire service. See 215.2(A)(3).If the rating, does not include the actual size of the fuse, you could put any size smaller than 100amp main in a dwelling