Sorry for a re-post, but my follow-up question got buried in the thread, so here it is..
Others here pointed me to 200.6 and 250.119 about whether it is OK to re-identify an ungrounded conductor as a neutral or an EGC when it's a part of a cable assembly.
So I'm reading the exceptions now and trying to understand what "Where the conditions .. ensure that only qualified persons" means -- industrial/commercial only?
"Where the conditions of maintenance and supervision ensure that only qualified persons service the installation, [grounded or EGC] conductors in multiconductor cables shall be permitted to be permanently identified at their terminations at the time of installation."