However, the NEC Handbook is not enforceable and does not constitute formal interpretations of the NFPA.
I am fully aware of that fact and there are members here that are very tired of me pointing that exact fact out. :grin:
"neither the NFPA nor the contributors to this handbook guarantee the accuracy or completeness of or assume any liability in connection with the information and opinions contained within this handbook."
I have posted it myself in the past.
When I brought the handbook up in repose to mxslick it was just as another opinion.
Additionally, I, along with several other people in this forum disagree that the Code permits the conduit to be supported by the truss framing members without also securing it per 358.30(A) because 358.30 requires compliance with both (A) and (B).
What do you think the code required in the 1996, 1999 and 2002 cycles now that I posted them?
The Code does not say "either (A) or (B)" - it says comply with both (A) and (B), period.
Which is a mistake on the 2005 CMPs part.
If you can provide a Code reference where it says that if the EMT is supported by framing members every 10 feet then it doesn't need to be secured per 358.30(A), I'll buy in.
I believe I have done so for 96, 99 & 02.
But until then, I'm standing my ground, along with several other people in this forum, many of which are inspectors and the very people who can make your life difficult.
Just as the handbook is just an opinion so is the opinion of inspectors. Inspectors, just like electricians are known to make mistakes.
Is there any doubt that securing the EMT per 358.30(A) in addition supporting it per 358.30(B) results in a safer installation?
That is an entirely different subject, we are talking what the NEC requires.
You make it sound like securing the EMT per 358.30(A) would be a bad thing.
No, that is not what I mean or think. I think misunderstanding the rules is a bad thing.
If the CMP truly means to disregard 358.30(A) if the installation complies with 358.30(B), then securing it per 358.30(A) is going above what is required for the benefit of everyone involved.
Now that is simply not true.
A common application of this allowance is EMT run horizontally through holes in studs that are fairly close fit to the EMT and will be covered by wall finish. In a case like that additional 'securing' would not provide any benefit making it only a waste of money for both the EC and the customer.
The end user gets a safer installation and the electricians make a little more money.
That depends on so many things, if the customer asked for a code minimum bid the EC losses money if they go beyond it.
Now most of the jobs I work on are engineered jobs with detailed specifications that require us to go beyond the minimums and that is great, I am very happy to work beyond code when I can get paid for doing so. After it is all said and done I do this to make money.