When you cut EMT you should always ream it correct? Would the same go for RTRC conduit? THanks
When you cut EMT you should always ream it correct? Would the same go for RTRC conduit? THanks
Applies to RMC, IMC, PVC, etc.
EMT
358.28 Reaming and Threading
(A) Reaming. All cut ends of EMT shall be reamed or otherwise
finished to remove rough edges.
RTRC
355.28 Trimming. All cut ends shall be trimmed inside
and outside to remove rough edges.