Circuits go from 120/208v panel to relay panel then from relay panel to receptacle. That's how it's wired.I don't see 18awg running to a receptacle in your link. Probably 18awg is only used for the relay control circuit.
I think you are getting it wrong. The circuit that supplies power to the receptacle must still be rated for the receptacle load, e.g 14 or 12awg typically.Circuits go from 120/208v panel to relay panel then from relay panel to receptacle. That's how it's wired.
My question is I don't think you run 600V #12's to the receptacle from the relay panel. Think you run low voltage #16 or #18.
[QUOTE="jaggedben, post: 2757519, member: 129901"]
I think you are getting it wrong. The circuit that supplies power to the receptacle must still be rated for the receptacle load, e.g 14 or 12awg typically.
The link you posted doesn't show any receptacles. It only shows relay controls. Your low voltage wiring is between your relay panel and the relay controls.