Pierre C Belarge said:Norb
We do that already...over on the other site. :grin:
OK, let us all in on the secret, where is the "other site"?
Pierre C Belarge said:Norb
We do that already...over on the other site. :grin:
iwire said:You can install the receptacle.
You will not be able to plug a cord into it. 400.8(5)
realolman said:why would it be ok to use flexible cord under a raised floor, but not above a suspended ceiling?
realolman said:So...how does one connect cord and plug connected things in these locations?
realolman said:I read it with my own eyes, so there it is, but it doesn't make much sense to me...
inspector23 said:This code section is my main point when I am trying to convince my jurisdiction not to allow cord-connected furnaces in the attics of the tract homes.
stickboy1375 said:I don't get it? We're talking about suspended ceilings, your talking about an entire floor level...
inspector23 said:Section 400.8
Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following: #(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings.
inspector23 said:Section 400.8
Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following: #(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings.
iwire said:So as I am sitting here in my basement all flexible cords on the first and second floors are in violation of 400.8(5) because they are concealed from me by ceilings?
I can't buy that all, but I do agree cord is not a great choice for a furnace.
Section 400.8
Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following: #(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings.
stickboy1375 said:I really don't believe an attic is concealed by a ceiling... Unless of course there is no attic access...
inspector23 said:Here is what I confuses me -
If the attic access is what determines that a cord can be used above a ceiling, (because you have access) then why can't you use a cord above a suspended ceiling? All those ceiling tiles could be removed just as easily as the attic access.
What am I missing????
hillbilly1 said:Would hardwiring it and using a switch as the disconnecting means violate the UL listing?
hillbilly1 said:Would hardwiring it and using a switch as the disconnecting means violate the UL listing?
Dennis Alwon said:Possibly but installing that type of unit in a suspended ceiling may also be a violation.