So one of my guys fouled up and forgot to run a circuit for a receptacle to satisfy 210.63 I think I have a solution but want to put it out there and see what you guys think
For the current setup right now is I have a mini split unit with a MCA of 20 amps and a MOP of 25 amp.
We have a number 10 from the panel going out there my plan was to put a 35 amp breaker in the main into an outdoor splice box
from an outdoor splice box Mount to disconnects one fused at 25 amps for the AC unit and one fuse at 15 amps for a service receptacle basically using the number 10 as a feeder and tapping it
Anybody see any issues with this. I wasn't sure if you use 35 amps or 30 for that feeder