I'm having some difficulty with this requirement. The reasoning for this Code section as you stated is so that lamp cords won't get heated, dried out and/or cooked. I can understand that if the BB heat unit was a hot, glowing element. However, in the case of hot water BB heat units or an electric hydronic type BB heat unit I don't see how that could happen.A lamp cord that's plugged into a standard receptacle over a baseboard heater will be "cooked" by the rising heat and degrade over time which could lead to electrical fires.
Liability... you bet that why it says what it says in the listed equipment instructions.
I'm having some difficulty with this requirement. The reasoning for this Code section as you stated is so that lamp cords won't get heated, dried out and/or cooked. I can understand that if the BB heat unit was a hot, glowing element. However, in the case of hot water BB heat units or an electric hydronic type BB heat unit I don't see how that could happen.
Aside from the fact that it is electrically operated, what is the difference? The heating unit is not designed to put out more heat than a hot water baseboard unit.There is no prohibition for hot water baseboard heat. If the manufacturer of electric hydronic baseboard heaters wants to allow the receptacles they can.
Heat density is the difference.Aside from the fact that it is electrically operated, what is the difference? The heating unit is not designed to put out more heat than a hot water baseboard unit.
Aside from the fact that it is electrically operated, what is the difference? The heating unit is not designed to put out more heat than a hot water baseboard unit.
Ok. I'll buy that.:thumbsup:Heat density is the difference.
Typical electric baseboard heater is 250 watts per linear foot. Should you come up with one that is only 100 watts per foot it may not get hot enough to be a problem for cords plugged into a receptacle above it.
Hydronic baseboards - mostly will depend on boiler output temperature and other conditions for how much heat you get at a particular point in the system. Such systems you very well may find the temp at the beginning of a zone is higher then near the end of the zone. Such systems typically have lower heat density in a baseboard then an electric baseboard has though, and because of this you find a hydronic baseboard often runs nearly entire length of a wall or even wraps around corners in a room, where if you were to put electric baseboard heater in same room wouldn't need to be so long to get same heating capacity - higher heating density.
I would guess that at any point along the electric baseboard the temperature exceeds several hundred degrees. Most hot water systems use a water temperature at the boiler of about 180 degrees which is diminishes as you move away from the boiler. At that temperature it is not high enough to melt a cord.