Shaneyj
Senior Member
- Location
- Katy, Texas
- Occupation
- Project Engineer
Thank you for the response sir, I was hoping you would chime in...Your guess is correct
That appears to be a G&W VIPER ST
Sometimes know as a “triple single”.
Meaning it will open all three phases or a single phase at a time depending on how you want it set up with the control relay.
I set them up for single phase operate, three phase lockout.
Exactly rightThank you for the response sir, I was hoping you would chime in...
Single phase operate: does that mean on a fault it will only open the faulted phase during the reclosing sequence but then open all 3 of it goes through its duration (number of clearing attempts - not sure the lingo) and fault still exists?