this doesnt say anything about color
IMHO the red color is not an issue, the issue is making sure that the cable has the proper listing for the application. For example if the low voltage lighting system is a class 2 system and the fire alarm cable is a listed class 2 cable and is installed in accordance with Parts I and III of Article 725 then it would be OK.
Chris
I would agree for a building that doesn't have a fire alarm. But if the same cable is used in the same building for fire alarm wiring, aren't we defeating the purpose of making the fire alarm cable readily identifiable??
I would agree for a building that doesn't have a fire alarm. But if the same cable is used in the same building for fire alarm wiring, aren't we defeating the purpose of making the fire alarm cable readily identifiable??
I don't see how Chaper 9, T11A enters into this. That table shows the ratings for the power supply. If the power supply is a listed Class 2 power supply as required by 411.3(B) there is no reason to look at T11AFire alarm cables are not required to be red, unless it is a local code.
I am going to shoot from the hip and say it is not permitted.
The change in Article 411 is not a wholesale change permitting just any Chapter 725 cable for these applications. One is also required to apply Table 11A from Chapter 9. There is more to this than just the cable type, the overcurrent protection is very specific.