Red on terminal bar?

Status
Not open for further replies.

tonype

Senior Member
Location
New Jersey
Need help... 3 circuits that I normally see wired as MWBC have red conductors connected to the terminal bar (also double-lugged). I have never seen this...any insight would help.
 

Attachments

  • DSCF2464.jpg
    DSCF2464.jpg
    152.1 KB · Views: 0
As Jumper stated, since there already is a white conductor landed, red as the EGC is my guess.
 
I see paper around the wires, so I think it is AC cable.
Whoever wired this doesn’t understand that the jacket on AC is the EGC. :lol:
 
I see paper around the wires, so I think it is AC cable.
Whoever wired this doesn’t understand that the jacket on AC is the EGC. :lol:

NM also has paper in it. I'm on the "old 3-wire" band wagon, white= neutral, red=egc although they could have either stripped it or taped it green.
 
But you can't re-identify a conductor smaller than #8 unless it's a traveler or the white of a 2 conductor cable used for 220, no?



-Hal

Actually it's #4 and larger

Legally, no. Common sense, sure you can.

220 is load calc.

See 200.

I think by "220" he was referring to 220V or what should be called 240V. Like using 10-2 and identifying the white as a hot (ungrounded) conductor.
 
Actually it's #4 and larger



I think by "220" he was referring to 220V or what should be called 240V. Like using 10-2 and identifying the white as a hot (ungrounded) conductor.

Hal was referring to the noodle in a multi conductor cable. 200.7 I think, not size dependent for that section.

And yeah, I got the voltage reference wrong.

We both missed!:D

Edit: I just reread Hal.:ashamed1:

I missed twice.:slaphead:

I am never coming back to this thread.....
 
Last edited:
One other question on this... is there any problem with the conductor cutting across the panel between the main and other breakers?
 
Legally, no. Common sense, sure you can.

220 is load calc.

See 200.

Ok, so haven't looked at this in many years and my memory isn't what it used to be anyway. Yes, Art. 200 refers to the grounded conductor (neutral). Side note: I don't agree with not allowing #6 and #8 to be re-identified as a neutral with white tape like you can with #4 and larger. For whatever reason they had, copper was cheap then. Having to stock several reels instead of only one can be costly today.

Now talking about grounds. What article talks about the grounding conductor and not allowing say a red #12 to be re-identified with green tape for a ground? Used to be common to do this with IG receptacles. Jog my memory.

-Hal
 