I have an outbuilding with an 8 slot MLO subpanel. It is fed with a 60A feeder from the house from a 60A breaker at the house panel. The subpanel has 3 DP breakers (15A, 15A, 40A), a SP breaker (15A), and 1 empty slot. Inspector says I need a main because I don't have a single disconnect rated at 60 amps. The panel itself is suitable for use as Service Equipment and is rated at 125 amps.
Since I'm using the 6 disconnect rule, how have others determined the disconnect rating when you have "grouped" disconnects? I would think you would sum the breakers and hope you get at least 60. Or maybe this is a group of branch circuits disconnects, so each breaker must only be 15A or more... This seems legal to me and I'm thinking of challenging it. Any suggestions? This is in Washington State.
Since I'm using the 6 disconnect rule, how have others determined the disconnect rating when you have "grouped" disconnects? I would think you would sum the breakers and hope you get at least 60. Or maybe this is a group of branch circuits disconnects, so each breaker must only be 15A or more... This seems legal to me and I'm thinking of challenging it. Any suggestions? This is in Washington State.