Jim
Why waste the ink?The requirements for a disconnect require that it be SUITABLE for use as service equipment. It doesn't say you have to use it as such.
If it is safe enough to be used as a power panelboard with six disconnects, how can it not be safe for use a lighting and appliance use?
Does not have an exception as (B) does below.408.36 Overcurrent Protection
(A) Lighting and Appliance Branch-Circuit Panelboard Individually Protected
And don't ask me why cause I don't know.(B) Power Panelboard Protection
Exception: This individual protection shall not be required for a power panelboard used as service equipment with multiple disconnecting means in accordance with 230.71.
Jim