Here is a photo of a 208V 3Ø feed (since removed) using 12 AWG green conductors in a circa 1968 Zinsco panel.



In the past it seems it was more tolerated to use green as hots, but it is just another example to never trust what you see.
 
Are you saying
If I pull a NM cable from point A to point B and in the middle of the run I bend the cable in half but don't cut it and shove it into a single gang box for a future outlet then go back and strip the outside sheath off of the NM in that box but don't cut the wires that I have to re sheath it or I've created a code violation if I don't terminate?

Or leave a stripped NM folded up but not terminated in a panel?
We are talking cable terminations, not conductor terminations. Where the sheath is stripped from cable, a cable termination is created. If the sheath is stripped from a cable in the middle, you then have at least 4 cable terminations, regardless of whether the conductors are cut or terminated.
 
We are talking cable terminations, not conductor terminations. Where the sheath is stripped from cable, a cable termination is created. If the sheath is stripped from a cable in the middle, you then have at least 4 cable terminations, regardless of whether the conductors are cut or terminated.

I'm not following you.


JAP>
 
Once the sheath is removed from the cable, you must either make a compliant cable termination or re-sheath the cable. In this vain, a cable will always have two ends and no exposed conductors in between ends.

A string of piercing type temp lighting on a run of romex would not satisfy this rule.

JAP>
 