I wouldn't. For all the obvious reasons.Say you are running conduit to a clothes dryer 2 black 10 AWG. 1 green 10 AWG. but you have no white 10ga. could you run a 12?
Why don't you use the green 10awg and phase it white? Then phase your #12 green? Then you are legal so to speak!
250.119 Identification of Equipment Grounding Conductors.
Unless required elsewhere in this Code, equipment
grounding conductors shall be permitted to be bare,
covered, or insulated. Individually covered or insulated
equipment grounding conductors shall have a continuous
outer finish that is either green or green with one or more
yellow stripes except as permitted in this section. Conductors
with insulation or individual covering that is green,
green with one or more yellow stripes, or otherwise identified
as permitted by this section shall not be used for ungrounded
or grounded circuit conductors.
It looks to me like 210.19(A)(4) would allow this.
(4) Other Loads. Branch-circuit conductors that supply
loads other than those specified in 210.2 and other than
cooking appliances as covered in 210.19(A)(3) shall have
an ampacity sufficient for the loads served and shall not be
smaller than 14 AWG.
Exception No. 1: Tap conductors shall have an ampacity
suffıcient for the load served. In addition, they shall have
an ampacity of not less than 15 for circuits rated less
than 40 amperes and not less than 20 for circuits rated
at 40 or 50 amperes and only where these tap conductors
supply any of the following loads:
(a) Individual lampholders or luminaires with taps extending
not longer than 450 mm (18 in.) beyond any portion
of the lampholder or luminaire.
(b) A luminaire having tap conductors as provided in
410.117.
(c) Individual outlets, other than receptacle outlets,
with taps not over 450 mm (18 in.) long.
(d) Infrared lamp industrial heating appliances.
(e) Nonheating leads of deicing and snow-melting
cables and mats.
Exception No. 2: Fixture wires and flexible cords shall be
permitted to be smaller than 14 AWG as permitted by
240.5.
I considered the possibility prior to my first post. But in reconsidering...This covers taps and fixture wire? I am not saying that you are wrong, just that I do not see a neutral conductor following tap rules.
......... but what would prevent someone from plugging in something that puts more than 20amps on the noodle? ..........
who knows what, you never know (which is what the NEC writes code for). shouldn't all CCC's be sized to the receptacle's amp rating?.....such as, what?
.....such as, what?
The general rule of 210.19(A)(4) looks quite tempting, but you can't use #12 on a greater than 20A circuit per 240.4(D)(5)... as a normal circuit conductor. As a tap conductor, perhaps 210.19(A)(4) Exception No.1 item (c). I get two different interpretations when reading that item. Is it saying individual receptacle outlets are okay... or not okay?
Outlet. A point on the wiring system at which current is
taken to supply utilization equipment.
your view of outlet is correct. but perhaps "receptacles" are excluded by that 18" verbiage?Well, IMHO no since its saying other than receptacle outlets. A receptacle is an outlet, but not all outlets are receptacles. Here is the definition of outlet:
I could be very wrong though.
(b) The minimum branch-circuit conductor size shall have an allowable ampacity not less than the maximum load to be served after the application of any adjustment or correction factors.
but
210.19 in 2017 nec
where exactly would you be getting a "load" # for a dryer ??
GE dryer i lookup simply says "25A", thus all CCC's that has 25A min ampacity after all adjustments, which puts it back to #10.[/FONT][/COLOR]