peter d
Senior Member
- Location
- New England
a 2-pole 3 CCC dryer, you calculate neutral amps how exactly? for that matter, a 2-pole 3 CCC NEMA 14-, the neutral calc is what ??
this is why i am saying just match the wire to the recept accordingly. 14-50 needs #6 NM, or #8 THHN in conduit. i dont see where NEC stops #8 NM to a 14-50 as long as OCPD is no more than 40A, there is no 14-40 to use, etc. but i see where folks may see a 14-50 and think the ckt is good for 50 if they swap out the 40 to a 50 ocpd.
this falls into same argument of running #14 to 20A rated recepts using 15A ocpd. seems plausible, very possible that someone uses a real 20A device and keeps tripping breaker, but then they decided to swap the breaker to a 20A = bad.
with a dryer on a 14-30, #10 will be min wire size, so if the ocpd was for some reason a 25a ocpd and i swapped that to a 30a, no issue.
What other people do with my installations is of no concern to me whatsoever. Please stop trying to put your theoretical "what ifs" into real world situations, you have no practical experience as an electrician and shouldn't be lecturing us on what should and shouldn't be done.