#10 will (should) have a -30R. if a 30A ocpd doesnt hold then there is some other problem.For those worried about what someone may plug in there down the road - how can you control that even if you ran 10 AWG for all conductors? Then if the breaker doesn't hold how do you prevent them from swapping with a higher setting breaker? You can only design/install for what you have now, you can't "what if" proof everything, an improved idiot will eventually find a way of messing it up.
if you run say #10 to 14-50 and use a 14-50P on the dryer (if it fits ok and is not prohibited), and the ckt has 30A ocpd. ok thats fine, all is protected, except now you have an idiot hazard up front, the 14-50 yells out "i am 50 amps able", but the ocpd doesnt say so, and idiot doesnt really know what awg means, so they swap out 30A for a 40 or 50 ocpd. if the dryer ckt was wired using 14-50R and wire to support 50A ocpd but you install 30A ocpd, thats fine, its also idiot proof.
i feel like some are contradicting NEC intent, which is for the most part, is to be idiot proof within reason.