Reduced neutral to dryer

Status
Not open for further replies.
but then maybe OP didnt give correct info, maybe it is conduit to a NEMA? post #1 does not suggest that, but who knows. hard wire or not, where in NEC is the exception that allows downsize of a CCC for a 2-pole 3CCC dryer ?

Perhaps. But it's not worth my time to thumb thru to some rarely used (or conflicting) NEC section, or figure out motor vs heater FLA, etc. to avoid pulling in #10 as a dryer neutral. I'm going to pull in #10, be done with it, and onto the next job in less time than it's taken to reply here. and not give 2c about the extra $0.14 worth of copper I used pulling in a #10 vs #12.

Real world.
 
Perhaps. But it's not worth my time to thumb thru to some rarely used (or conflicting) NEC section, or figure out motor vs heater FLA, etc. to avoid pulling in #10 as a dryer neutral. I'm going to pull in #10, be done with it, and onto the next job in less time than it's taken to reply here. and not give 2c about the extra $0.14 worth of copper I used pulling in a #10 vs #12.

Real world.
i agree with you. was just following the thread which made some references that "would/might" allow such, etc. hence i think we are all kinda wondering what the real Q is in post #1, or why that Q is asked that way. its an old Q, http://forums.mikeholt.com/showthread.php?t=85868&page=2
 
i agree with you. was just following the thread which made some references that "would/might" allow such, etc. hence i think we are all kinda wondering what the real Q is in post #1, or why that Q is asked that way.

My first thought was it was a test/instructor question... 'is there ANY instance where you can use a #12 grounded/#10 ungrounded and grounding conductors to a dryer'? type thing. Dont care. #10 all the way around and done, unless this was something like a coin operated unit in a hotel that is 300' from the panel, then as iwire mentioned I'd be looking at VD.

~~~~~~~~~~~~~

Some of you guys might be able to remember every little exception in the NEC. I cannot. If I am in doubt I'm going above code (or its exceptions) unless material cost to do so merits research. I dont believe that the case here.
 
This thread is about a hard wired dryer.

That never even entered my mind and I still would say that is a 0.001% chance of being a hard wired dryer.


All Im saying is that 110.3(B) can come into play, as those are part of the instructions.

I agree. :)

The mfg also spec'd copper wire. You might be able to land #8 or #6 on the lugs; that is meeting or exceeding mfg install instructions, and I wouldnt have a problem with doing such for voltage drop. #12 is not #10 or better, so imho using it to hardwire a dryer like the one I linked instructions to would be a violation.

Hold on, you are telling us that 'use number 10 AWG" is a listing instruction but we can ignore it if we go bigger.

I think you are winging it. :)



And again, I highly doubt this thread is about a hardwired dryer.
 
post #1 ???

not, "conduit to receptacle"
yes?
While I concur hard-wired is possible, I automatically assumed receptacle. Perhaps that's just as bad as gleaning it is hard wired from "running conduit to a clothes dryer".

I'll still say my assumption has a better probability of being correct. :lol:
 
That never even entered my mind and I still would say that is a 0.001% chance of being a hard wired dryer.
And again, I highly doubt this thread is about a hardwired dryer.

Say you are running conduit to a clothes dryer .......

so right away you assume its conduit to a NEMA recept? you're not even near 50/50 ??? using jbox and flex it would certainly be very valid to keep people from unplugging a possibly coin operated dryer and using the power for free. maybe Mr Jones put in a coin operated dryer in his house to make the kids pay-for-use and dont want anyone doing anything they should not be doing with a receptacle if it were there ??? who knows, but 0.001%, really?

I'll still say my assumption has a better probability of being correct. :lol:
well, at this point, some us us think its flex (conduit) to the dryer, some of you believe otherwise. from interpreting the words of post #1, i myself did not assume receptacle, but think maybe the OP may have asked w/o good clarity. see post #63 if you missed that.
 
Last edited:
Perhaps. But it's not worth my time to thumb thru to some rarely used (or conflicting) NEC section, or figure out motor vs heater FLA, etc. to avoid pulling in #10 as a dryer neutral. I'm going to pull in #10, be done with it, and onto the next job in less time than it's taken to reply here. and not give 2c about the extra $0.14 worth of copper I used pulling in a #10 vs #12.

Real world.

Yeah, it's the difference between a theoretical/classroom discussion and the real world. In the classroom the question is "what is the minimum conductor size for this application?" whereas the real world question is "will the #10 I have in the truck work?" :D
 
so right away you assume its conduit to a NEMA recept?

Yes, that is how single phase LL/LN 30 amp dryers are wired.




using jbox and flex it would certainly be very valid to keep people from unplugging a possibly coin operated dryer and using the power for free. maybe Mr Jones put in a coin operated dryer in his house to make the kids pay-for-use and dont want anyone doing anything they should not be doing with a receptacle if it were there


If you don't use a receptacle you have to install a disconnect switch or breaker lock, that being the case most electricians go for a cord and plug.
 
Yes, that is how single phase LL/LN 30 amp dryers are wired.


If you don't use a receptacle you have to install a disconnect switch or breaker lock, that being the case most electricians go for a cord and plug.

the GE dryer (a single phase LL/LN appliance) instructions show how to wire using conduit.

and your point about disco/lockout is not relevant to the OP's question.

next?
 
the GE dryer (a single phase LL/LN appliance) instructions show how to wire using conduit.

and your point about disco/lockout is not relevant to the OP's question.

next?

Actual electricians don't think about this stuff. We run a smaller neutral and move on to the next job.
 
Actual electricians don't think about this stuff. We run a smaller neutral and move on to the next job.
are you saying electricians just dont think? i suspect not.
ok, where in NEC does it allow you to use #12 N for a 1-phase 2-pole 3CCC ~25A dryer (hard wire or receptacle)? i patiently waiting. i myself cant find it, but maybe i missed it.
 
who knows what, you never know (which is what the NEC writes code for). shouldn't all CCC's be sized to the receptacle's amp rating?

7080333__85990.1450869003.500.750.jpg

Let's see the listing for that dogbone......
 
a 2-pole 3 CCC dryer, you calculate neutral amps how exactly? for that matter, a 2-pole 3 CCC NEMA 14-, the neutral calc is what ??

Is nothing in NEC that specifically addresses this AFAIK. Experience does tell me that for the most part there is a (maximum) 1/2 hp 120 volt motor in such appliances, possibly a 120 volt lamp that is maybe 25 watts maximum, and either a mechanical or electronic timer control that usually operates at 120 volts as well. I don't expect there to be more then 10 amps maximum on the neutral conductor. If you can find a model with more neutral load then that feel free to post links to the specifications of that model.

are you saying electricians just dont think? i suspect not.
ok, where in NEC does it allow you to use #12 N for a 1-phase 2-pole 3CCC ~25A dryer (hard wire or receptacle)? i patiently waiting. i myself cant find it, but maybe i missed it.
Ca n you find anything that prohibits it? Like I mentioned earlier there is minimum grounded conductor sizes mentioned in 215 for feeders and for services you get to jump around a little bit but there is a minimum size, I haven't ever found such requirement in 210 for branch circuit grounded conductors.

For those worried about what someone may plug in there down the road - how can you control that even if you ran 10 AWG for all conductors? Then if the breaker doesn't hold how do you prevent them from swapping with a higher setting breaker? You can only design/install for what you have now, you can't "what if" proof everything, an improved idiot will eventually find a way of messing it up.

As far as people plugging other items into range or dryer outlet - I'd say over 99% of what I have ever seen has either no neutral or about as minimal of a neutral load as the range or dryer has, exception may be for 50 amp receptacles supplying a camper, job trailer or something of that nature, but in those cases they generally are not plugging into a receptacle located specifically in a place for a range but rather the same 14-50 type of receptacle in a non kitchen location.
 