Ingenieur

Senior Member
Location
Earth
Point taken. The OP is in Indiana, so they are still on the 2008 code and the latest changes wouldn't apply, unless the machine is considered "industrial" (Article 409 covers "Industrial" control panels and was introduced in the 2005 code).

PS: Actually, the relevant wording hasn't really changed since the 2005 code. 409 requires it for "industrial controls", then defines that. But 430.8 requires it as well, for "motor controllers" in general.


MSHA uses 1968
iirc PA recently went to 2008 from 2002
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Hmmm...
Having the correct SCCR at the panel and having it meet or exceed the AFC is now a CODE REQUIREMENT.
Your methodology, while probably good for a guesstimate (I'm not doing the math), is NOT going to suffice in lieu of a proper fault study and the required labeling.

Proper SCCR has been a Code requirement for decades. But because everyone seems to have routinely ignored 110.10, the CMP's have been adding additional SCCR requirements to other code articles as well.
 
I am going to nitpick on a couple points.... Sorry :angel:

you need a calculation that has been signed and sealed by an engineer regularly engaged in the practice of calculating fault currents.

you want to ask if they have an existing short circuit study or set of plans listing the amount of fault current available at the equipment.

Unless someone is asking who has authority or you need to listen to, I dont see why this would necessarily need to be done by an engineer. Basic fault current calculations are very easy and can be done by a competent electrician. Sure, get into a bunch of motor contribution, or a more complex system then maybe you will need an engineer to be involved.

I would add that the available fault current has to be obtained from the utility and be careful that you are not provided with the standard utility response of an infinite bus fault current based on transformer size.

I dont quite follow you here. First where is it stated that it "has to be obtained from the utility"? Perhaps it is a local requirement, but the NEC does not contain such language. If you do obtain the value form the utility, I think 94% of the time you will get their generic response. IMO and experience, if you dont want the generic figure, you have to calculate it yourself from the actual equipment data and still good luck getting any information on the primary impedance. Maybe you mileage has varied in that department. Finally, for AIC purposes, there is nothing wrong with using a higher than actual fault current value (other than possibly spendng money on unneeded AIC, but sometimes worth the simplicity).
 

drktmplr12

Senior Member
Location
South Florida
Occupation
Electrical Engineer
Unless someone is asking who has authority or you need to listen to, I dont see why this would necessarily need to be done by an engineer. Basic fault current calculations are very easy and can be done by a competent electrician. Sure, get into a bunch of motor contribution, or a more complex system then maybe you will need an engineer to be involved.

someone regularly involved in calculating available fault current, in any case. the path of least resistance would be an existing study, assuming someone knows where to look inside said study
 

wbdvt

Senior Member
Location
Rutland, VT, USA
Occupation
Electrical Engineer, PE
In the previous posts, there has been discussion on the NEC for code compliance regarding SCCR. What is overlooked quite frequently is the OSHA requirement below:

1910.303(b)(5)
Circuit impedance and other characteristics. The overcurrent protective devices, the total impedance, the component short-circuit current ratings, and other characteristics of the circuit to be protected shall be selected and coordinated to permit the circuit protective devices used to clear a fault to do so without the occurrence of extensive damage to the electrical components of the circuit. This fault shall be assumed to be either between two or more of the circuit conductors, or between any circuit conductor and the grounding conductor or enclosing metal raceway.


This seems to indicate that all the equipment in the circuit has to be suitable for the fault current. So having properly rated equipment installed is also an OSHA requirement.
 

kwired

Electron manager
Location
NE Nebraska
I am going to nitpick on a couple points.... Sorry :angel:



Unless someone is asking who has authority or you need to listen to, I dont see why this would necessarily need to be done by an engineer. Basic fault current calculations are very easy and can be done by a competent electrician. Sure, get into a bunch of motor contribution, or a more complex system then maybe you will need an engineer to be involved.



I dont quite follow you here. First where is it stated that it "has to be obtained from the utility"? Perhaps it is a local requirement, but the NEC does not contain such language. If you do obtain the value form the utility, I think 94% of the time you will get their generic response. IMO and experience, if you dont want the generic figure, you have to calculate it yourself from the actual equipment data and still good luck getting any information on the primary impedance. Maybe you mileage has varied in that department. Finally, for AIC purposes, there is nothing wrong with using a higher than actual fault current value (other than possibly spendng money on unneeded AIC, but sometimes worth the simplicity).
:thumbsup:

If you don't know actual primary impedance yet still calculate service fault current based on infinite primary - and your values at load end devices is under their rating - you are fine with equipment selected, it will only get lower if you did figure out actual primary values. You don't even need to fully know how to calculate this, just need to know how to read transformer impedance off the nameplate, need to know how to determine conductor size, type, length, and a few other reasonably simple details and enter that information into spreadsheets that are readily available out there and can easily come up with values that are "worst case scenario".
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This is an interesting thread especially for us non-engineers who don't deal with this stuff very often. There seems to be some opinions that this is a very complex question and some other opinions that it really isn't. So getting back to the OP where it said this:

We installed several 30 & 60 amp type TEY 14K AIC 3 phase breakers. Ran the conduit and wire to where each new machine. Each machine has 3 fuses that our feeds connect to. Just received a call from the company that the machine manufacture wants the AIC on some of the machines to be 10K AIC

We have a circuit breaker and some conductors in a branch circuit feeding a piece of equipment. Given the information above it is difficult to do the calculation and find the answer to the OP's question?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
This is an interesting thread especially for us non-engineers who don't deal with this stuff very often. There seems to be some opinions that this is a very complex question and some other opinions that it really isn't. So getting back to the OP where it said this:



We have a circuit breaker and some conductors in a branch circuit feeding a piece of equipment. Given the information above it is difficult to do the calculation and find the answer to the OP's question?
:thumbsup:

For a branch circuit, especially one of significant length, the impedance of the circuit conductors should limit the AFC (Available Fault Current), possibly enough to solve the whole problem.
 

Ingenieur

Senior Member
Location
Earth
there was a thread recently that had links for a checklist of requirements for a code review/permit app process
it required utility furnished primary values
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
This is an interesting thread especially for us non-engineers who don't deal with this stuff very often. There seems to be some opinions that this is a very complex question and some other opinions that it really isn't. So getting back to the OP where it said this:



We have a circuit breaker and some conductors in a branch circuit feeding a piece of equipment. Given the information above it is difficult to do the calculation and find the answer to the OP's question?

Rob,
This is the problem with the OP's statement as it stands:
...machine manufacture wants the AIC on some of the machines to be 10K AIC...
That statement as typed is not using valid terms and makes no sense. MACHINES cannot have an "AIC", only the BREAKERS can. On top of that, an "AIC rating" on a breaker is a "not to exceed" value and the ones he ALREADY installed are 14kAIC, so wanting them to have a lower interrupting capacity value is ridiculous; the breakers he provided ARE at least 10kAIC, in fact they are 40% MORE than 10kAIC. So their "want" is indicative of someone in this situation not knowing what they are talking about. I'd hazard a guess that the machine manufacturer is not saying it right, and the OP didn't quite know enough to push back yet. Hence my attempt to edumacate him and have him go back to get them to say what they REALLY need.
 

topgone

Senior Member
Rob,
This is the problem with the OP's statement as it stands:

That statement as typed is not using valid terms and makes no sense. MACHINES cannot have an "AIC", only the BREAKERS can. On top of that, an "AIC rating" on a breaker is a "not to exceed" value and the ones he ALREADY installed are 14kAIC, so wanting them to have a lower interrupting capacity value is ridiculous; the breakers he provided ARE at least 10kAIC, in fact they are 40% MORE than 10kAIC. So their "want" is indicative of someone in this situation not knowing what they are talking about. I'd hazard a guess that the machine manufacturer is not saying it right, and the OP didn't quite know enough to push back yet. Hence my attempt to edumacate him and have him go back to get them to say what they REALLY need.

Agree. If the installed breakers' AIC is more than the available short circuit fault in the location, there is no problem.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
:thumbsup:

For a branch circuit, especially one of significant length, the impedance of the circuit conductors should limit the AFC (Available Fault Current), possibly enough to solve the whole problem.

It's been a long time since I did any of these calculations but that was my original thought. He's at no more than 14 AFC at the CB, if we assume that the panel has been installed properly (with all the necessary calculations and equipment to match), can we calculate what the available short circuit current will be at the equipment at the end of the branch circuit if we know the conductor size and the length of the branch circuit, etc.?

Again I'm an old bucket of rust when it comes to this stuff so I'm asking and feel free to correct my terminology if it's incorrect. :)
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Agree. If the installed breakers' AIC is more than the available short circuit fault in the location, there is no problem.
The point is that although there is no problem with the breakers and conductors there may be a problem with the maximum AFC allowed by the makers of the machine or the specifying engineer.
That may have been specified using the wrong vocabulary, but could still be a problem.

Sent from my XT1585 using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The point is that although there is no problem with the breakers and conductors there may be a problem with the maximum AFC allowed by the makers of the machine or the specifying engineer.
That may have been specified using the wrong vocabulary, but could still be a problem.

I have seen labels on equipment stating that there is a limit to the maximum AFC that the equipment can withstand. We had a thread many years ago about a dimming panel that had such a limitation and the manufacturer recommended using certain length of conductor to lower the AFC at the panel.
 

topgone

Senior Member
The point is that although there is no problem with the breakers and conductors there may be a problem with the maximum AFC allowed by the makers of the machine or the specifying engineer.
That may have been specified using the wrong vocabulary, but could still be a problem.

Sent from my XT1585 using Tapatalk

Could have been a wrongly specified equipment then? If the system in place has an available fault current at a certain location, the specifier should take note of that limitation and order the equipment with such short circuit capacity rating, or better!
 

MyCleveland

Senior Member
Location
Cleveland, Ohio
Could have been a wrongly specified equipment then? If the system in place has an available fault current at a certain location, the specifier should take note of that limitation and order the equipment with such short circuit capacity rating, or better!
Soooo agree...with the new 2017 NEC label requirements at so many locations, everyone will catch on quickly when EI's start telling them to replace IT.

Just from today, a air-compressor vendor that I had notified months ago the fault current at his equipment would be 21k, the shop drawing came through stating equipment rated at 5k.

8 or 9 emails later, it will now arrive with a FACTORY label of 65K SCCR.
 
Last edited by a moderator:

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Could have been a wrongly specified equipment then? If the system in place has an available fault current at a certain location, the specifier should take note of that limitation and order the equipment with such short circuit capacity rating, or better!
I think a big problem here is that "specifiers" don't yet realize that they need to include an appropriate SCCR as a requirement. So vendors, fearful of adding cost and losing an order, take advantage of the omission and go with the cheapest thing they can find; an untested electrical assembly that gets the "courtesy" listing of 5kA SCCR.

I think by now most people building electrical equipment KNOW this is an issue, but some don't divulge it (willingly). Not a month goes by that I don't get a call from someone asking me how they can lower the AFC at a jobsite, because something came in with an SCCR label saying 5kA and they have 23kA, 44kA, 65kA or something like that available at the terminals, a fact that they discover only after the AHJ red tags it.
 

retirede

Senior Member
Location
Illinois
Soooo agree...with the new 2017 NEC label requirements at so many locations, everyone will catch on quickly when EI's start telling them to replace IT.

Just from today, a air-compressor vendor that I had notified months ago the fault current at his equipment would be 21k, the shop drawing came through stating equipment rated at 5k.

8 or 9 emails later, it will now arrive with a FACTORY label of 65K SCCR.

I’d love to know what make of compressor since I worked in that industry for years.
 

kwired

Electron manager
Location
NE Nebraska
It's been a long time since I did any of these calculations but that was my original thought. He's at no more than 14 AFC at the CB, if we assume that the panel has been installed properly (with all the necessary calculations and equipment to match), can we calculate what the available short circuit current will be at the equipment at the end of the branch circuit if we know the conductor size and the length of the branch circuit, etc.?

Again I'm an old bucket of rust when it comes to this stuff so I'm asking and feel free to correct my terminology if it's incorrect. :)

I have seen labels on equipment stating that there is a limit to the maximum AFC that the equipment can withstand. We had a thread many years ago about a dimming panel that had such a limitation and the manufacturer recommended using certain length of conductor to lower the AFC at the panel.

One thing that OP has not revealed yet is size and length of branch conductors. I recall mentioning of 30-60 amp circuits, so we are talking about relatively small conductors - those cut down AFC pretty quick. Using fault current calculator that is available on Mike Holt's web site I put in 14kA as a starting point and 25 feet of #6 copper - that knocked 14 k down to 9.2k and 50 feet knocks it down to 6.9k. those are both relatively short distances for circuit length in many industrial environments.

Soooo agree...with the new 2017 NEC label requirements at so many locations, everyone will catch on quickly when EI's start telling them to replace IT.

Just from today, a air-compressor vendor that I had notified months ago the fault current at his equipment would be 21k, the shop drawing came through stating equipment rated at 5k.

8 or 9 emails later, it will now arrive with a FACTORY label of 65K SCCR.

if label says 5k they never tested anything - that is default when not tested.

You want more then that you pay for the label (even if they had already tested it before your request)
 