I am going to nitpick on a couple points.... Sorry :angel:
Unless someone is asking who has authority or you need to listen to, I dont see why this would necessarily need to be done by an engineer. Basic fault current calculations are very easy and can be done by a competent electrician. Sure, get into a bunch of motor contribution, or a more complex system then maybe you will need an engineer to be involved.
I dont quite follow you here. First where is it stated that it "has to be obtained from the utility"? Perhaps it is a local requirement, but the NEC does not contain such language. If you do obtain the value form the utility, I think 94% of the time you will get their generic response. IMO and experience, if you dont want the generic figure, you have to calculate it yourself from the actual equipment data and still good luck getting any information on the primary impedance. Maybe you mileage has varied in that department. Finally, for AIC purposes, there is nothing wrong with using a higher than actual fault current value (other than possibly spendng money on unneeded AIC, but sometimes worth the simplicity).