petersonra
Senior Member
- Location
- Northern illinois
- Occupation
- engineer
I think a big problem here is that "specifiers" don't yet realize that they need to include an appropriate SCCR as a requirement. So vendors, fearful of adding cost and losing an order, take advantage of the omission and go with the cheapest thing they can find; an untested electrical assembly that gets the "courtesy" listing of 5kA SCCR.
I think by now most people building electrical equipment KNOW this is an issue, but some don't divulge it (willingly). Not a month goes by that I don't get a call from someone asking me how they can lower the AFC at a jobsite, because something came in with an SCCR label saying 5kA and they have 23kA, 44kA, 65kA or something like that available at the terminals, a fact that they discover only after the AHJ red tags it.
I think it is unfair to blame this on the equipment manufacturers. We have a form to be filled out and one of the things on the form is SCCR required. Very few customers bother to provide a number. A fair number write in "N/A".
It is not as big a deal these days, at least for us, but a few years ago there was a huge difference in cost between a UL508a panel rated at 10 kA SCCR and one rated 65 kA. The cost difference is somewhat less these days as long as end users are flexible on parts, especially if they are willing to accept fuses.
I mention 10 and 65 kA because I find that most of the time going above 10 kA gets you to 65 kA anyway. There are only a few cases where I have run into something in between. It happens but is not real common.