Think of it as a thread evolving....
Sent from my XT1080 using Tapatalk
Sent from my XT1080 using Tapatalk
and this has something to do with the OP and Refrigerator no longer allowed in garage?
Do the covers meet 410.10(D)?
(D) Bathtub and Shower Areas. No parts of cord-connected
luminaires, chain-, cable-, or cord-suspended luminaires, lighting
track, pendants, or ceiling-suspended (paddle) fans shall
be located within a zone measured 900 mm (3 ft) horizontally
and 2.5 m (8 ft) vertically from the top of the bathtub rim or
shower stall threshold. This zone is all encompassing and includes
the space directly over the tub or shower stall. Luminaires
located within the actual outside dimension of the bathtub
or shower to a height of 2.5 m (8 ft) vertically from the top
of the bathtub rim or shower threshold shall be marked for
damp locations, or marked for wet locations where subject to
shower spray.
8' above the tub or shower threshhold niether applies and subject to shower spray is judgemental -- you do know under an exterior eve is considered damp , tell me you never saw a plastic or metal blank plate covering an exterior luminaire opening and if so did you fail the final -- open bulb recess trims are damp rated are there j boxes rated for damp locations?
I was referring to the J box of the recess can -- which is generall exposed to atmosphere