210.17 Electric Vehicle Branch Circuit. Outlet(s) installed for the purpose of charging electric vehicles shall be supplied by a separate branch circuit. This circuit shall have no other outlets.
Informational Note. See 625.2 for the definition of "Electrical Vehicle".

1.) NEC Section/Paragraph: 210.17 (new)
2.) Comment Recommends: Deleted Text.
3.) Proposal/Comment: Reject the proposal.
4.) Substantiation: Panel 2 is once again venturing into design considerations without minding the impositions of vague and unenforceable language on both installers and inspectors trying to comply with the Code, and without evidence of a problem relating to safety or fire hazard. The panel is creating a problem where the installer may claim it is for a blender and the inspector claims it looks like an EV-charging location. This is a design consideration based on equipment that may not have even been invented yet. See the panel's more appropriate responses to proposals 2-63 and 2-64. There may be instances where the designer finds it beneficial to group an EV receptacle with other loads for other purposes.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I guess you don't like what was accepted. BTW, the submitter is CMP2 so do they just accept their own proposal-- they can't loose can they.
 