kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
If the control circuit is class 2 or 3, the nipple into the RIB is listed but whatever you supply it with needs to have separation between class 2/3 conductors and power conductors. It doesn't necessarily need to be a barrier that separates them though.Excuse my ignorance but having never used a relay in a box I'm guessing there is not a need to install a barrier between the high and low voltages? Does that only apply to switches?
Class 1 control circuit would not require any separation at all.