I have the following circuit:
How do I comply with transformer primary protection in accordance with NEC 2017?
The internal transformer is a 24VAC, 1.2VA, class 2 transformer.
I read Article 430.72.
Article 430.72(C)(3) states:
I have the following circuit:
- 20A branch circuit breaker
- Aube RC840T-120 (Electromechanical relay with 120V/24V transformer for a 24V control signal)
https://customer.honeywell.com/en-US/Pages/Product.aspx?cat=HonECC+Catalog&pid=RC840T-120/U - 24V thermostats
- 115V 0.8A hydronic unit heater
How do I comply with transformer primary protection in accordance with NEC 2017?
The internal transformer is a 24VAC, 1.2VA, class 2 transformer.
I read Article 430.72.
Article 430.72(A) states:
"General. A motor control circuit tapped from the load
side of a motor branch-circuit short-circuit and ground-fault
protective device(s) and functioning to control the motor(s)
connected to that branch circuti shall be protected against
overcurrent in accordance with 430.72. Such a tapped control
circuit shall not be considered to be a branch circuit and shall
be permitted to be protected by either a supplementary or
branch-circuit overcurrent protective device(s) [...]"
side of a motor branch-circuit short-circuit and ground-fault
protective device(s) and functioning to control the motor(s)
connected to that branch circuti shall be protected against
overcurrent in accordance with 430.72. Such a tapped control
circuit shall not be considered to be a branch circuit and shall
be permitted to be protected by either a supplementary or
branch-circuit overcurrent protective device(s) [...]"
Article 430.72(C)(3) states:
"Less Than 50 Volt-Amperes. Control circuit transformers
rated less than 50 volt-amperes (VA) and that are an integral
part of the motor controller and located within the motor
controller enclosure shall be permitted to be protected by
primary overcurrent devices, impedance limiting means, or
other inherent protective means."
rated less than 50 volt-amperes (VA) and that are an integral
part of the motor controller and located within the motor
controller enclosure shall be permitted to be protected by
primary overcurrent devices, impedance limiting means, or
other inherent protective means."