So, you aren't sure if a 15 or 20 Amp 125 Volt duplex receptacle on a single yoke is an Article 100 Definitions "Device"?
I know perfectly well what a device is and that it applies to receptacles. I'm just not certain that the intention of 210.12(B) Exc. is to trump 406.4(D)(4).
You keep harking back to non-Code text in the ROP and Analysis of Changes. I prefer to look at the
Code text:
(B) Branch Circuit Extensions or Modifications ? Dwelling Units.
In any of the areas specified in 210.12(A), where branch-circuit wiring is modified, replaced, or extended, the branch circuit shall be protected y one of the following: ....
Exception: AFCI protection shall not be required where the extension of the existing conductors is not more than 1.8 m (6 ft) and does not include any additional outlets or devices.
Once again this is an exception to 210.12(B) which tells you that when you extend or change a branch circuit in an area that s required to have AFCI protection according to 201.12(A), then you must protect it. The exception tells you that under limited circumstances you need not AFCI protect an extension.
Note that 210.12(B) does not mention replacement receptacles, only wiring. So replacing a receptacle under 406.4(D)(4) is not covered by 210.12(B) and is therefore not covered by the exception. I do not know how to make it any clearer and thus this is my final attempt.
Fmtjfw, is this, then, your showing me in the language of the NEC that a receptacle device replacement requires AFCI? All I can tell is that you underlined the readily accessible requirement.
Now, I do understand that you WANT AFCI required at ANY receptacle device replacement, but I can't find that statement of requirement in 406.4(D)(4). What you WANT, and what the Code says, may not be the same.
And I note that you WANT the statement of requirement for AFCI limited to the list of locations in 210.12(A), but, again, I don't see "as specified elsewhere in this Code," as providing you that limitation.
At the bottom of my long screed about this I indicated that
underlined denoted text added to 2014. This is the text with the gray background in 2014.
I want any receptacle in a location required by current
Code to be ACFI protected, to be AFCI protected, and I don't want any interpretation of 201.12(B) Exc. to interfere with that.
I have not altered the text of 406.4(D)(4) in this forum thread.