And I wonder how long it will be before someone introduces a dual function receptacle device? Or will there just not be enough room in a single gang box for one?
If they can fit dual function into a single breaker space, I fail to see why they can't put the electronics into a duplex which fits in a single gang box. How many years was it between GFCI breaker and receptacle???And I wonder how long it will be before someone introduces a dual function receptacle device? Or will there just not be enough room in a single gang box for one?
Third choice...
Dual Function breaker and standard receptacle.
Have at it. Got about two months left... to get it in for 2017.Perhaps a code proposal is in order.
Since we are directed to "elsewhere in the NEC" I believe that includes the Exception to 2014 210.12(B). If the conductors are at all short (and in many cases in the older installs they are) the existing conductors invite the installation of pigtails. Adding conductor less that six foot in length invokes the exception to 210.12(B), and no AFCI protection is needed whether the old two wire nongrounding type receptacle is replaced with a GFCI receptacle, or a similar new nongrounding type receptacle.
Code understanding, this is the heart of the issue, IMHO. 406.4D4 doesn't, on it's own, require AFCI, no way, no how. 406.4D4 ONLY refers us to " elsewhere in the NEC."
Therefore all of 210.12 applies as it fits the situation, including on replacements.
Tapatalk
From the 2011 NEC 406.12:
Respectfully, you are mis-reading me. I understand the exception to the TR requirement that is offered for non-grounding type receptacles. My point, my meaning, is as stated in Post #16 .You are misreading the exception. It refers to 2 prong receptacles without a grounding hole, not a 3 prong receptacle with a grounding hole but not connected to a EGC. All AFCI and GFCI receptacles I have ever seen include a grounding hole and thus do not fall under the no-TR exception.
Set the idea of TR that I introduced to the side. Just look at 406.4(D)(4). 406.4(D)(4) does not, all by itself, require AFCI, it only tells us to go "elsewhere in this Code".All AFCI and GFCI receptacles I have ever seen include a grounding hole and thus do not fall under the no-TR exception.
Respectfully, you are mis-reading me. I understand the exception to the TR requirement that is offered for non-grounding type receptacles. My point, my meaning, is as stated in Post #16 .
Today, IMHO, if I replace a bad duplex 15 or 20 Amp 125 Volt receptacle device, grounding or non-grounding type, and I choose to ADD 6 inch pigtails on the existing conductors, then 2014 NEC 210.12(B) Exception applies, and "no AFCI is required."
However I totally disagree with the idea that adding conductor within a box triggers 210.12(B) Exception. The exception allowing an extension of 6 feet of conductors makes it plain to me that the intent is that the extension is not in the box. You can code lawyer your interpretation, but it stretches the bounds of credulity. I hope you assertion is a rhetorical device and nothing that you would actually implement or allow.
I definitely would not want to be testifying in court, after the fire, that I decided not to install the Code-required AFCI based on that reasoning about the exception.
I am not the only one who can read this in the 2014 National Electrical Code as printed. Do you have a copy of the International Association of Electrical Inspectors (IAEI) Analysis of Changes NEC - 2014? Please refer to the very last sentence at the bottom of page 64:However I totally disagree with the idea that adding conductor within a box triggers 210.12(B) Exception.
Analysis of Changes NEC - 2014
210.12(B) Exception
"This will clarify that extending branch circuit conductors within an enclosure for the purposes of replacing a device or utilization equipment or for extending a branch circuit to a panelboard being replaced or upgraded does not require an AFCI protective device to be installed."
I read and understand that you, in your opinion, disagree with my point of what the 2014 NEC 210.12(B) Exception says. Please show me, with the language of the 2014 Code, how AFCI is "Code-required" when, after extending the branch circuit conductors less than six feet, only the replacing of a receptacle outlet device occurs (no new outlet added).I definitely would not want to be testifying in court, after the fire, that I decided not to install the Code-required AFCI based on that reasoning about the exception.
The NEC Committee Report on Proposals 2013 contains the following concerning the adoption of the 210.12(B) Exception:
"2-115 Log #536 .... 'Exception: AFCI protection shall not be required where the extension of the existing conductors is not more than 1.8 m (6 ft) and does not include any additional outlets or devices.' ....
. . .
Comment in Affirmative:
HILBERT, M: Continue to accept in principle. The issues noted in the substantiation are often topics of discussion at IAEI meetings as well as other educational meetings and do need clarification.
The proposed language as revised by the panel's accept in principal action will go a long way in promoting uniform interpretations. It will clarify that extending branch circuit conductors within an enclosure for the purposes of replacing a device or utilization equipment or for extending a branch circuit to a panelboard being replaced or upgraded does not require an AFCI protective device to be installed.
Six feet was chosen for branch circuit extensions as it should provide a sufficient length for most applications where an existing panel is being relocated out of a clothes closet or to comply with readily accessible requirements, etc."[ROP]