Now, what was it you wanted me to trust you about?
About the point I made in #7.
But if you still have doubts, open a thread regarding universal applicability of any of the rules of NEC, if you really care.
Now, what was it you wanted me to trust you about?
Please state the significance of 0.8 pf on the name plate of an alternator.Did you read my comment about thermal limits?
We build for and supply into Saudi Arabia. Do you?About the point I made in #7.
But if you still have doubts, open a thread regarding universal applicability of any of the rules of NEC, if you really care.
No but see belowWe build for and supply into Saudi Arabia. Do you?
if you still have doubts, open a thread regarding universal applicability of any of the rules of NEC, if you really care.
In means 0.8 pf.Please state the significance of 0.8 pf on the name plate of an alternator.
Why is it 0.8pf, not 0.9 or unity pf? or Why is it mentioned at all?In means 0.8 pf.
No?No but see below
All equipment covered by this specification shall be according to the requirements of the latest
edition of the following documents:
60044, 60051, 60073, 60044, 60044-5, 60255, 60269, 62052.11, 60947, 61641?.
Is that a test question?Why is it 0.8pf, not 0.9 or unity pf? or Why is it mentioned at all?
Maybe the 50Hz from the OP could have have clued you in.
You will of course, with your encyclopedic knowledge of all matters electrical, know that those required standards are IEC.
An enlightenment question.Is that a test question?
Do you need enlightenment?An enlightenment question.![]()
An enlightenment question.![]()
Any chance you two could take this outside so we could maybe hear from the OP again?Do you need enlightenment?
Going back to testing the generator at .8 PF: ....
Going back to testing the generator at .8 PF:
It is true, for the most part, that you could test the generator windings, etc. with a resistive load of 1.25 times the rated kW (corresponding to the current at rated KVA at .8 PF.) But I would be concerned that the prime mover could not support that, hence the need for a reactive load to set up the high current test.
Gold,Going back to testing the generator at .8 PF:
It is true, for the most part, that you could test the generator windings, etc. with a resistive load of 1.25 times the rated kW (corresponding to the current at rated KVA at .8 PF.) But I would be concerned that the prime mover could not support that, hence the need for a reactive load to set up the high current test.
Just resistive at 1.0pf would correspond to rated current. So 500kW. No need for reactance to get that. No need for the 1.25 times the rated kW.Going back to testing the generator at .8 PF:
It is true, for the most part, that you could test the generator windings, etc. with a resistive load of 1.25 times the rated kW (corresponding to the current at rated KVA at .8 PF.) But I would be concerned that the prime mover could not support that, hence the need for a reactive load to set up the high current test.
Just resistive at 1.0pf would correspond to rated current. So 500kW. No need for reactance to get that. No need for the 1.25 times the rated kW.
Just resistive at 1.0pf would correspond to rated current. So 500kW. No need for reactance to get that. No need for the 1.25 times the rated kW.
No.You do not agree that the load current in the generator windings will be greater at 630 kVA than at 500kW?