Yes. A hallway 10' or longer must have at least one.The hallway still requires receptacles.
Yes. A hallway 10' or longer must have at least one.The hallway still requires receptacles.
But wouldn't have to put one in front of a railing. Could be on a wall elsewhere.The hallway still requires receptacles.
What is the area where this banister is? If it is a 10' long or longer hallway, isn't that an out, as a hallway doesn't follow the 6/12 rule.
Yes it does, but as mentioned doesn't need to follow the 6/12 rule. neither does a foyer. But if there is sufficient enough amount of railing that a receptacle would still be required you probably using a floor outlet or some the other not so desired options brought up in this thread. To have this problem with a hallway you about need to have railing on both sides of said hallway for it's entire length though.The hallway still requires receptacles.
Maybe a catwalkTo have this problem with a hallway you about need to have railing on both sides of said hallway for it's entire length though.
Would be a pretty rare thing I would think in dwellings, but someone will think of a reason here or there to have something like that.Maybe a catwalk
I have, too. And that should be counted separately from any loft area on either end. Not real practical to require a receptacle there, but technically.....I have seen 'catwalks' in homes. More like a 'bridge'
What code wording do you think may require a receptacle there? The closest thing I can see in 210.52 is a hallway but IMO that is not a hallway.I have, too. And that should be counted separately from any loft area on either end. Not real practical to require a receptacle there, but technically.....
It serves the same purpose as any other hallway, just open-air instead of enclosedWhat code wording do you think may require a receptacle there? The closest thing I can see in 210.52 is a hallway but IMO that is not a hallway.
Same purpose or not IMO calling a catwalk a hallway is a stretch.It serves the same purpose as any other hallway, just open-air instead of enclosed
I’m going to play stupid Sam here a minute..You could stub up two RMC elbows and use a threaded hub box which wouldn't require support but for the rest of us a floor box is the only option.
I don't believe you would consider the larger area at the far end to be a space that needs to utilize the 6-12 spacing rules either, it is more "hallway".I have seen 'catwalks' in homes. More like a 'bridge'.
I don't believe you would consider the larger area at the far end to be a space that needs to utilize the 6-12 spacing rules either, it is more "hallway".
If that is so no reason a receptacle on the conventional "wall(s)" cans serve as the required receptacle for this "hallway".
Worst case where the centerline changes, you may need to consider to be separate hallways?
On something like this absolutely. Something more defined by code can be more debatable. Not saying you will get your way, just is more debatable.Again, it's not what I think, what I consider, what I call it.
It's what the AHJ think, considers, and calls it.
I’m going to play stupid Sam here a minute..
How would you trim this out to look acceptable?
I’m kinda like the others and thought floor box was the only option.