Excellent point, 300.15 “Fittings and connectors shall be used only with the specific wiring methods for which they are designed and listed.”Ok, I was up for this challenge of, is it legal to run one mombo Pvc connector to run a whole panels branch circuit system through, which I've seen and to me is lazy as , well you know ...
If I was an Inspector I'd say .. check 334.30 ... right were is says within every support within 12" of enclosure such as outlet boxes cabinet or ( fittings ) the key word is then fittings or should I say approved fittings, a pvc fitting does not maintain the clamp or crimp that a NMB connector possesses, So the argument would then be, what is an approved soft sheathed connector, does it need to be lightly compressed to prevent slippage. Anyone care to contribute to the question of using a pvc fitting or even just a large chase nipple. Besides I'm sure there's a violation just by having 3" of cables crammed together like that.
check 334.30 (A) other than they refer to horizontal I'm sure the NEC board would consider this as an applicable situation, as noted : and the non metallic sheathed cable is securely fastened in place by an approved means of each .. .. cabinet .. ( or other non metallic cable termination )
PVC connectors are not non metallic cable termination fittings.
The standard used to investigate products in this category is ANSI/UL 514B
From the UL white book section:
NONMETALLIC-SHEATHED-CABLE CONNECTORS (PXJV):
“MARKINGS
Connectors which are also suitable for use with service-entrance cable, flexible nonmetallic tubing or flexible cord are so indicated on the device or carton.
Except for duplex connectors or when otherwise marked on the carton to indicate connecting of more than one cable or cord, the connectors covered under this category have been investigated for connecting one cable or cord
only.”
“RELATED PRODUCTS
Connectors covered under Armored Cable Connectors (AWSX), Conduit Fittings (DWTT) and Power and Control Tray Cable Connectors (QPOZ) are also suitable for use with nonmetallic-sheathed cable when specifically indicated on the device or carton.
Connectors suitable for flexible cord only are covered under Outlet Bushings and Fittings (QCRV).”
No mention of a PVC fitting.