Just bought a place and want some more opinions on what i have and if its correct. Metal frame dock, walkway and swim ladder are bonded #6, top of walkway at shore bonded to ground rod with #6. Stiff arm on other end of dock is not bonded. I believe it should be. Outdoor panel at top of walkway at shore is a main lug panel fed from the house, 4 wire system on standard two pole breaker. 4 gfci breakers in outdoor panel feeding individual branch circuits on the dock. All device boxes on the dock are bonded and made up to the ground bar in the outdoor panel, however the ground source for the outdoor panel is the ground coming from the house. It is not bonded to the ground rod. Neutral and ground are not bonded in the outdoor panel, I don't believe they should be, however I feel like the ground bar should also have a #6 going to the rod. Confused about the rule stating the feeder has to have its own egc. Also should there be a main breaker in the outdoor panel? Code states there must be a disconnecting means at the shoreline/top of walkway, do the breakers count as a disconnecting means or are they trying to specify ONE disconnect to de energize everything??