Motor conductors are sized to the full load ampacity of the motor (and usually to 125% of FLA). Then we have two types of overcurrent protection - the branch circuit device is usually the one that appears to be high - but is only intended to provide short circuit and ground fault protection, the motor overload protection not only protects the motor from overload but also protects the conductors from overload. Between the two protection types (if applied properly) that conductor is better protected from overcurrent then some general purpose circuits are.Ive never understood that. I could understand welders because they are intermittent (duty cycle), but why are motors allowed to load conductors to the max?
14, 12, and 10 are rated higher than 15, 20, and 30 amps the small conductor rule just limits them to that size overcurrent protection.But even at 125%, conductors can still see loading over 15, 20 and 30amps. Then again you do have a point that general use circuits tend to see more over loading.
You seem to be convinced that the NEC limits are not already conservative.
do they?But even at 125%, conductors can still see loading over 15, 20 and 30amps. Then again you do have a point that general use circuits tend to see more over loading.
But all that was exceeded was the 240.4(D) requirement (that doesn't apply to this install), the 14 AWG applied at 75C was still protected at less then it's capacity in T310.15(16).But that's my point in your example #14 is seeing more than 15amps. I guess the tables are conservative enough, but always wondered why less so for motors. I get the short circuit protection may be 250%, but that is for faults only.
And it is still rated at 20A on the seventy five degree scale and 25A on the ninety degree.But that's my point in your example #14 is seeing more than 15amps. I guess the tables are conservative enough, but always wondered why less so for motors. I get the short circuit protection may be 250%, but that is for faults only.
I have a HOA requesting validation that a cloths dryer 30 amp outlet would have had to been wired with #10 conductor during 1985 construction of the building.
The issue is, I had #12 feeding a 30A dryer outlet on 30A breaker and aware of this violation had it rewired correctly.
I need a validation that in 1985 this circuit conductor had to be #10 and that #12 would under no circumstance be proper for this 30A circuit.
No one that I know really knows where the table values come from, we just use them in along with other code sections for conductor sizing.But isn't that for de-rating only? I guess Im just confused why 240.4 (D) would limit the wire if it was safe.
I can't say I agree otherwise we wouldn't have the exceptions we have to 240.4(D). Not to mention a motor can actually contribute even more current into a fault.My understanding of the 'small conductor' rule is that it has to do with conductor damage during fault conditions, not overload.
The _ampacity_ of a conductor is the maximum amount of current which can be carried on a continuous basis without exceeding the temperature limit of the conductor or insulation.
The ampacity of the conductor is set by a combination of the heat produced by the conductor and the rate that this heat is dissipated to the environment. Take the same conductor and bury it in thermal insulation, and it has lower ampacity then if it is in free air.
Because small conductors have lots of surface area relative to the amount of conductor, they operate at lower 'circular mils per amp' (just look at the conductor ampacity tables, smaller conductors use less copper per amp). This is the reason that you can save copper by using conductors in parallel for large installations, and also the reason that larger circuits have less voltage drop over the same distance for their 'rated current'.
During a short circuit, currents far greater than the ampacity of the conductor will be carried until the OCPD operates. Smaller conductors operating at lower circular mils per amp will heat up more rapidly during a fault. To allow standard OCPD to protect the conductors during a short circuit, the 'trip rating' of the OCPD must be less than the continuous ampacity of the conductors.
-Jon