Example
A commercial office space will require fourteen 277-volt fluorescent lighting circuits to serve a single open office area. The office area lighting is assumed to be a continuous load, and the office ambient temperature will not exceed 30?C (86?F). Each circuit will be arranged so that it has a computed load not exceeding 16 amperes. The selected wiring method is Type MC cable, 3-conductor (with an additional equipment grounding conductor), 12 AWG THHN copper. Each individual MC cable will contain a 3-wire multiwire branch circuit. To serve the entire area, this arrangement will require a total of seven Type MC cables bundled for a distance of about 25 ft, without maintaining spacing between them where they leave the electrical room and enter the office area.
Determine the ampacity of each circuit conductor in accordance with 310.15, applying Exception No. 5 to 310.15(B)(2)(a) to account for the bundled cables. Then determine the maximum branch-circuit overcurrent protection permitted for these bundled MC cables.
Solution
Step 1.
To apply Exception No. 5, first determine the quantity of current-carrying conductors. According to 310.15(B)(5), equipment grounding conductors are not counted as current-carrying conductors. According to 310.15(B)(4)(c), fluorescent lighting is considered a nonlinear load, so the grounded conductor of each Type MC cable must be counted as a current-carrying conductor.
7 cables X 3 conductors each = 21 CCC
Because the quantity of current-carrying conductors exceeds 20, a 60 percent adjustment factor is required by 310.15(B)(2)(a), Exception No. 5.
From table 310.16, #12 THHN = 30A
30A X .6 = 18A
Step 2.
Determine the ampacity of each current-carrying conductor due to these MC cables with more than 20 current-carrying conductors being bundled.
Because the actual computed load is 16 amperes of continuous load, 210.19(A)(1) is applicable. The conductors must have an ampacity equal to or greater than the load before the adjustment factor is applied. Because the ampacity of the conductors after the adjustment factor is applied is 18 amperes, no further adjustment is necessary and the conductors are suitable for this installation.
Step 3.
Finally, determine the maximum size of overcurrent protection device permitted for these bundled MC cable branch circuits. Section 240.4(B) permits the use of the next higher standard rating of overcurrent protection device. Therefore, although the conductors have a computed ampacity of 18 amperes, a 20-ampere overcurrent protective device is permitted. In addition, and of significance, the 20-ampere overcurrent protective device is in compliance with 210.20(A), given that the actual 16-ampere continuous load would require a 20-ampere overcurrent protective device, based on the listing of the overcurrent device.