Had a final inspection completed today on a single family new build with a 2 car attached garage.
Couple of concerns from inspector.
- AHJ said that I needed to have a 120v receptacle located on the front wall of each vehicle space.
One side had one on the front wall, the other side had one on a sidewall . He said the sidewall one did not meet the requirement.
In addition to the two mentioned, there were a total of 3 more placed throughout the garage.
I could not find any mention of " front wall" in the code.
He also said that on a stairway in the garage leading down to the basement ,that there needed to be a light that was switched along with the lights above the steps inside the room in the basement.
The area he speaks of is located on the opposite side of a door.
I currently have 3 way switching for the lights above the steps in the garage, and a switch for the lights in the room once you open and pass through the door.
Have set up this type of switching on numerous houses through the years and never been called on it.
Couple of concerns from inspector.
- AHJ said that I needed to have a 120v receptacle located on the front wall of each vehicle space.
One side had one on the front wall, the other side had one on a sidewall . He said the sidewall one did not meet the requirement.
In addition to the two mentioned, there were a total of 3 more placed throughout the garage.
I could not find any mention of " front wall" in the code.
He also said that on a stairway in the garage leading down to the basement ,that there needed to be a light that was switched along with the lights above the steps inside the room in the basement.
The area he speaks of is located on the opposite side of a door.
I currently have 3 way switching for the lights above the steps in the garage, and a switch for the lights in the room once you open and pass through the door.
Have set up this type of switching on numerous houses through the years and never been called on it.