Residential heat-vent-light cabling
tkb
MA
I usually do commercial and industrial wiring, but I have to install a heat-vent-light w/night light in my mothers house.
This requires 4 hots, 1 neutral and a ground from the switches.
What is the normal practice for wiring this fixture?
Since there in no such thing as 12-5 NM cable, is using 2 cables, one 12-3 NM and one 12-2 NM acceptable?
This would mean that the neutral would be used in one cable, the other white would be reidentified and there would be 2 groung wires from the switches to the fixture.
Wiring diagram
Is this correct, or is there another way?
Thanks
Re: Residential heat-vent-light cabling
The neutral is common to all four loads?
Edit: You could just use two cables and if you keep them together you wont have an EMF issue.
[ November 08, 2004, 11:09 AM: Message edited by: physis ]
Yes, all four use the same neutral.
I don't think it's a problem with 2 cables, I was just asking if there is a diferent way.
I have some TC tray cable 6 conductor #12. Can type TC be used in a dewling unit? It seems that you could use it almost anywhere else.
Good question as to whether type TC can be used as type NM. Looks like 336.10(2) and 336.12(2) would prohibit it.
I have always wired these things with a 12/2 and a 12/3 as you suggest.
-Hal
I have found that ENT (smurf pipe) and a deep 5S box with 1 or 2 gang plater ring (depending on the control configuration) is the best solution for this, assuming this is new work.
Stranded #12 THHN is easier to use than the solid in the romex, especially in the cramped j-box on the heat/fan units.