I usually do commercial and industrial wiring, but I have to install a heat-vent-light w/night light in my mothers house.
This requires 4 hots, 1 neutral and a ground from the switches.
What is the normal practice for wiring this fixture?
Since there in no such thing as 12-5 NM cable, is using 2 cables, one 12-3 NM and one 12-2 NM acceptable?
This would mean that the neutral would be used in one cable, the other white would be reidentified and there would be 2 groung wires from the switches to the fixture.
Wiring diagram
Is this correct, or is there another way?
Thanks
This requires 4 hots, 1 neutral and a ground from the switches.
What is the normal practice for wiring this fixture?
Since there in no such thing as 12-5 NM cable, is using 2 cables, one 12-3 NM and one 12-2 NM acceptable?
This would mean that the neutral would be used in one cable, the other white would be reidentified and there would be 2 groung wires from the switches to the fixture.
Wiring diagram
Is this correct, or is there another way?
Thanks