roger said:
As far as not hearing about electrocutions caused by utility or privately wired metal pole lights, just keep searching, these occurrences have a way of being swept under the rug so to speak.
Roger,
Ahh..yes.. swept under the rug. With every attempt and success at concealment, comes the inevitable broad stroke of the brush. When an electrocution occurs, OSHA is called and a full detailed investigation is undertaken by both gov't and private investigators. The results of those investigations are sometimes less detailed than we would like. But aside from that, all electrocutions are summarized as event driven and may be as vague as 'direct contact with energized conductors'. But, within my company, the events are detailed and self explanatory, we have had electrocutions of contractors and employees setting poles, removing poles, rewiring in and on poles, thus the many areas of hazard.
Now to the safety of the general public in relation to metal poles. I agree more could be done.
For example lets assume a metal street light pole which has a 120v fixture is fed from a #4 cu UF direct buried underground cable approximately 20 feet from a 25KVA tx feeding several lights. Let's look inside the hand-hole where the wire terminates. We have 2-conductor (Hot and Neutral) #4 as the source, and 2 conductor with ground #14 as the load. We install an electrode and a bond of #4 cu to the pole ground lug and then ground electrode.
Now as you can see we have the pole grounded. Lets assume the 120v leg comes loose from the termination point and faults against the body of the pole. What happens next, is the fault current can create several different forms of outcome. Let's focus on the high impedance fault. Say the fault current generated is enough to open the #4 sol ground to the electrode, but not of enough magnitude or time to open the OCPD in the 25KVA tx (25,000 watts). What we are left with is 120v leg lying on a high impedance metal pole. An unsuspecting person can theoretically be electrocuted, because the only protection is the OCPD of the 25KVA tx. If a GFCI of 15 amperes were installed, yes it would be practically safer. IMO if one person in the general public were to be electrocuted in this fashion, I believe alternatives would be implemented. Therefore, I will consider metal poles a shock hazard, and as for electrocutions, I have no knowledge of any.