don_resqcapt19 said:
ServiceTech,
How do you feed dwelling units with a delta secondary?
Don
Don,
You can not derive 120/240v from a WYE tx bank connection.
Therefore if you have 120/240v you have a DELTA connection. 99.9% of our customers have a 120/240v service, thus a DELTA connection. Also, I might add this is not a true DELTA connection. A true DELTA does not have a ground. We have not had a true DELTA in years.
don_resqcapt19 said:
What is a "floating neutral"? Any neutral used as a circuit conductor must be a grounded conductor.Don
In industrial areas where the demand is for power and less for single phase loads, we supply a WYE-DELTA with a floating neutral. What that means is that we isolate the primary ground of the H2 bushing "float" and connect it to an open disconnect. When this arrangement is installed we have three tx's connected DELTA on the secondary which supplies equal balanced circulating current to each phase.
The impedance of the three tx's is critical at this stage, there can be no more than (if I remember correctly) 1.5% deviation of impedance between the three tx's. If one tx fails, a noticeable problem will be observed by the industry supplied, whereas we can respond and repair before the other tx's or cust equipment are damaged. If the "floating" neutral were directly connected, and a tx went off line, the customer would not see a problem. Because, the DELTA connection allows service to continue uninhibited without noticeable effects, until the other two tx's, which at this stage have been supplying the demand of the failed tx off line, fail due to overload and/or core meltdown.
Therefore for service reliablity and cost associated with a WYE-DELTA, the neutral is "floated". The reason the fourth (as we call it) disconnect is in place, is so we can safely trouble shoot this extremely hazardous arrangement.