kda3310
Senior Member
- Location
- Dry Prong, Louisiana
:? Where do I start to learn how to calculate how large of a meter can and panel I need for a residential service. I wired homes but would like to know how to calculate the service and panel sizes.
If you have Microsoft Excel you can scroll down and download this free calculator to check your answe:
That helps a lot. Thanks. However I need a little more help. I am doing this for a friend and he is trying to save as much money as he can. His feed will come up to his house under ground. A 50 foot run. He is responsible for the cost for that run so he wants to use aluminium. We have calculated he needs a 350 amp service. The residential calculator says we will need a 500 kcm aluminium feeder. How do I brake that down to run it parallel.
That helps a lot. Thanks. However I need a little more help. I am doing this for a friend and he is trying to save as much money as he can. His feed will come up to his house under ground. A 50 foot run. He is responsible for the cost for that run so he wants to use aluminium. We have calculated he needs a 350 amp service. The residential calculator says we will need a 500 kcm aluminium feeder. How do I brake that down to run it parallel.
You hinted that this house may be about 3000 Sq Ft. Even without details, experience tells me that 350 amps is probably about twice the size it should be.
You hinted that this house may be about 3000 Sq Ft. Even without details, experience tells me that 350 amps is probably about twice the size it should be.
Are you doing the Standard or Optional calculation? With two heat pumps, I'd go the optional