Residential smoke alarms

guschash

Senior Member
What code article would I find the requirements for installing smoke alarms in a residential setting. Beginning of 760 says they are not subject to requirements of article 760.
 

augie47

Moderator
Staff member
The location and mounting is normally addressed by the applicable Building Code in your area.
 

GoldDigger

Moderator
Staff member
What code article would I find the requirements for installing smoke alarms in a residential setting. Beginning of 760 says they are not subject to requirements of article 760.
The local building code will tell you what type of alarms are required, where they have to be located and whether they need to be interconnected.
NEC will tell you some additional information about acceptable wiring methods once you have the other information for your locale.
 

mwm1752

Senior Member
2009 IRC Smoke Alarms Art 314, Carbon Monoxide Alarms Art 315
Do you have a specific question?
 

iwire

Moderator
Staff member
How big of an area does one smoke alarm cover?
I don't believe they are installed like that.

Typically the rules will require one smoke alarm at specific locations.

Like 'provide one smoke alarm at each bedroom door' or provide one smoke alarm at the foot of the basement stairs.

They are not installed for full coverage like smoke detectors are in non-dwelling units.
 