Residential smoke alarms

Status
Not open for further replies.

guschash

Senior Member
Location
Ohio
What code article would I find the requirements for installing smoke alarms in a residential setting. Beginning of 760 says they are not subject to requirements of article 760.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The location and mounting is normally addressed by the applicable Building Code in your area.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
What code article would I find the requirements for installing smoke alarms in a residential setting. Beginning of 760 says they are not subject to requirements of article 760.
The local building code will tell you what type of alarms are required, where they have to be located and whether they need to be interconnected.
NEC will tell you some additional information about acceptable wiring methods once you have the other information for your locale.
 

iwire

Moderator
Staff member
Location
Massachusetts
How big of an area does one smoke alarm cover?

I don't believe they are installed like that.

Typically the rules will require one smoke alarm at specific locations.

Like 'provide one smoke alarm at each bedroom door' or provide one smoke alarm at the foot of the basement stairs.

They are not installed for full coverage like smoke detectors are in non-dwelling units.
 