That's not even close to being accurate.
That's not even close to being accurate.
I can guarantee the ones I installed would chirp on power loss. The battery was not low. I dealt with this for a few days while working there. They never chirped when the power was on. If the batteries were low, they would chirp with or without AC power.UL would never list a smoke alarms that chirped when loosing the primary power source. Homeowners would remove the alarms every time the power went off leaving no protection. They only chirp on low or no battery.
That's not even close to being accurate.
I was pretty surprised the AHJ viewed it that way, but he said there was no code definition of a fire alarm system, so if you have a 15A fire alarm circuit that only supplies a Non Power Limited Fire Alarm circuit (NPFLA) it falls under 760, and 760.3 rules out 210.Do you agree that is the intent ??
Then they were defective or something else was going on.I can guarantee the ones I installed would chirp on power loss. The battery was not low. I dealt with this for a few days while working there. They never chirped when the power was on. If the batteries were low, they would chirp with or without AC power.
You cannot say something in 760 applies unless all of the Article applies. For one the requirements for the powering of a fire alarm system required by Article 760 do not apply to residential smoke alarms. From Mike Holt:I was pretty surprised the AHJ viewed it that way, but he said there was no code definition of a fire alarm system, so if you have a 15A fire alarm circuit that only supplies a Non Power Limited Fire Alarm circuit (NPFLA) it falls under 760, and 760.3 rules out 210.
Article 760 covers the installation of wiring and equipment for fire alarm systems. Residential smoke alarm systems, including interconnecting wiring, are not covered by Art. 760 because they are not powered by a fire alarm system as defined in NFPA 72, National Fire Alarm and Signaling Code.
For some reason he thought that the power would need to originate at a fire alarm panel, A Non–Power-Limited Fire Alarm Circuit (NPLFA) does not need to originate at a fire alarm panel.Article 760 covers the installation of wiring and equipment for fire alarm systems. Residential smoke alarm systems, including interconnecting wiring, are not covered by Art. 760 because they are not powered by a fire alarm system as defined in NFPA 72, National Fire Alarm and Signaling Code.
These were not the 10 year batteries. They weren't defective either as they have been in for 2 years. Have you not ever seen a UPS unit that beeps when on battery power?Then they were defective or something else was going on.
No reputable manufacture would design a smoke alarm to beep on loss of primary source. Everyone I know, including myself would be removing them every time the power went off. Might as well not have a battery backup. At least you will have protection when the power comes back. If they get removed they may never get put back up.
If the smoke alarm is one of the 10 year battery models sometimes the battery does not get activated properly. My guys install the bases and pigtails during the main part of trim out. The smoke alarms don't get installed until all dusty activity, painting, etc. is done. Some Kidde models you had to turn the smoke alarms so hard to activate the batteries the base would move or come off the ceiling. They would keep one base off and use it to activate the alarms in their hands prior to installing on the ceiling.
If the battery didn't get activated properly they would beep low battery on power up. If you turned the power off they would still beep a couple time due to the stored charge in the smoke alarm.
A UPS is not a life safety device and the beeps can be turned off.These were not the 10 year batteries. They weren't defective either as they have been in for 2 years. Have you not ever seen a UPS unit that beeps when on battery power?
Just like you hearing that is a first for me but the inspector was completely incorrect in saying any part of 760 is applicable to the installation of 120 volt interconnected smoke alarms and in turn created a violation of 210.12(b)I was pretty surprised the AHJ viewed it that way, but he said there was no code definition of a fire alarm system, so if you have a 15A fire alarm circuit that only supplies a Non Power Limited Fire Alarm circuit (NPFLA) it falls under 760, and 760.3 rules out 210.