Hello what is the NEC code for residential smoke detector separation from walls ?
My understanding it can’t be placed in the first 4” from ceiling and wall , I was told it had to be install with in 12” .
 
This graphic may help with smoke alarm placement:
Where-to-install-smoke-alarms---Graph.png

Document

Welcome to the Forum. :)
 
Ok, if you had a vaulted ceiling that was 21’ to the peak, where would you guys put it? It must be serviceable right?


“ shoot low boys their riding shetland ponies”
 
Ok, if you had a vaulted ceiling that was 21’ to the peak, where would you guys put it? It must be serviceable right?


“ shoot low boys their riding shetland ponies”
At 21 feet, most designers would be considering beam detectors, but not for residential. You'll need a heck of an A-frame ladder or a Genie lift. See NFPA 72 for more discussion on smoke detectors/alarms on sloped ceilings.
 