I'm sure this topic has been kicked around before. I believe there is no maximum number of receptacles you can put on a 15 amp circuit in a residential dwelling, correct? With that being said, I was curious how many receptacles you prefer to put on a 15 amp circuit when you're roughing a house, what's your rule of thumb?
Do you keep your lighting on separate circuits, or do you combine lighting and receptacles together?
For today and for the future, as more and more homeowners adopt solar PV and battery backup systems, I recommend the following for new home builds or major renovations:
1. Keep all lighting circuits on 15A ckts that are separate from other loads and receptacles. These will be good candidates for moving to a critical loads subpanel that will be powered in a grid outage, providing much needed lighting when the grid is down.
2. Land equipment grounds and neutrals on separate busbars in the main service panel, and do not mix, even if the main N-G bond is made there. This will make it easier to move the main bond in the future if required by a larger solar PV installation.
3. Choose a main service panel with 225A bus (for 200A service) to permit larger PV inverter to be load side connected.
Apart from the above, I have other thoughts based on adding battery backup systems to existing homes, but probably too complicated to list details about it here as every home and family has different needs. But in general, if there is a load that most would consider important to keep running in a grid outage, and if that load is not a very big load, than putting those loads onto a few common circuits that would be candidates for the critical load subpanel would be helpful.
Also, my preference is 20A for general receptacle loads instead of 15A. Reduces the chance of tripping and having voltage drop issues on longer runs.